I would do the same... I'd run all three phases to your charging area. Then rectify the output and use thick cables to connect in a way that makes sense (in Series voltage is additive and current is the same Parallel voltage is the same and current is additive). Make sure you have a controller that can handle a worst case scenario...
Do what? I'm not sure what you're saying here.
I run five turbines - three of them on my house. When you run multiple turbines it's best to rectify at the base of the tower, install an outdoor DC junction box on the wall, and run DC power thru the wall into the building. That way you only have to make one installation in the house and as you add more more turbines you bury the wiring from the tower to the outside junction box and hook it into the DC bus in the box instead of drilling more holes in the wall.
Rectifying at the tower base requires either a manual shutdown at the tower base (which you should have anyway) or running a signal wire from the panel in the house to relays in the tower base junction for remote shutdown capability. I'm sure there's other ways to do it, but that's the way I've done it because it's nice to be able to shut down a turbine from inside the house when it's raining cats and dogs outside and the wind is blowing at 60 mph. Therefore, when you run the DC service thru the wall put enough 12 AWG wires in the conduit, terminated in the outside box on one end, and in the indoor panel on the other end, so you have a separate shutdown signal wire for each turbine you plan to add in the future. If you plan on running three turbines eventually - put five shutdown signal wires in the conduit. If you never use two of them, big deal. Always put in more than you think you need.
You can also run a separate AC service thru the wall for each turbine, if you don't mind drilling more holes in the wall. But if you have a long wire run from the tower to the house, you get less losses with DC than you do AC. So regardless, I think rectifying at the tower base is the way to go for a multiple turbine installation that's being used to charge batteries.
Henry mentioned a standby generator. Keep in mind that if you live off-grid, have a battery bank, turbines, solar, etc., your standby generator should be a battery charging unit, NOT a 120/240 AC unit. If you use 12 or 24 volt you can build a standby generator out of a small gas engine driving an automotive style alternator like I use:
This thing will put out 30 amps with the engine just idling and will run for three hours on 4-1/2 pints of gas. If you use 36 or 48 volt you can build an axial turbine generator and drive it with a low rpm engine of some sort for standby power.
If you don't have grid power don't even THINK about buying an inverter/charger - they're the most useless unit on the planet when you don't have grid power. Using a 120/240 volt standby generator to make AC power to run the charger in the inverter while it powers your house in AC bypass mode is just a way to waste fuel running the generator because generators like that have to run at full bore to make AC power, while a battery charging standby can run at very slow speed.
--